I have an intelliflo pump. I’m purchasing an ultra temp 110. I see in the installation manual in order to run “autoset” you will need to wire the autoset contractor to the time clock, where the pump is also wired. The issue here is the intelliflo is not wired to the time clock because it has its own digital clock. So I can I have the heater and pump communicate for this feature? Is there a cable that can connect the two to “talk”?

Please Sign In to post comments
Richard's picture
Tech, Pentair
Because the vs pump is
Richard's picture
Tech, Pentair
Posted

Because the vs pump is running in a free-standing mode, the heat pump will not communicate with the heat pump via 485 communication, I would recommend a type of control starting with a Suntouch, Easytouch or Intellitouch panel, this will allow the heat pump and vs pump communicate with each other via rs485 communication.